11-10-2012, 01:03 PM
(11-10-2012, 10:36 AM)pwdrive Wrote: Thanks Mark, been reading up also, some of these internet forums are lethal!! According to IEE (I think) PME can be exported to a domestic outbuilding but if there are any conductive pipes within the building then they must be bonded and connected to the suppliers earth back at the house using 10 mm/2 (cross sectional square area) earthing cable. But apparently exporting PME to say caravan pitches and livestock buildings is a no no. Just to re iterate my caravan is not a old style aluminium caravan, it's basically a wooden chalet but constructed so as to satisfy the legal definition of a caravan just in case the planners have anything to say!
I'd seen that IEE document about the PME supply to the garage before, and upon re-reading it, it's surprising that no mention is made of the O/C Neutral problem. Even when it goes on to discus what to do in the event of metal pipes in the garage, it doesn't mention this as a reason to go down the TT route.
If I was in your shoes, I reckon that I'd want to convert the whole of the dwelling into TT. It's just a case of removing the connection between earth and neutral, and providing an earth spike - and making sure that all circuits in the property at RCD-protected. It's the sort of job that you ought to pay for, simply to get all the certification for when you come to sell the house. Oh, and that's the law

If your dwelling was converted to TT in the future, then it would make sense to extend the earth out to the caravan. So if you said that you are going to extend the PME earth now, fully aware of the risks, but with a medium-term view to converting the whole property to TT, that would be an outcome I'd be comfortable with

Incidentally, with your current PME supply, I'd be tempted to connect a mains lamp of some sort, and perhaps a buzzer, between neutral and and earth spike - this would hopefully give you decent warning of an O/C neutral condition.
The likelihood of an O/C neutral might seem fairly low, but the consequences of it are pretty dangerous. So, in "risk assessment" terms, where we would multiply the likelihood times the consequences, this would merit some action...
Quote:I have just been outside to check the SWA cable it's three core (3x 10mm square) So does that mean that I can use the spare 10mm conductor as an exported PME earth, I will not hold anyone to their answers, just trying to get a general consensus at the moment.
Yes, everything I've read says that this is fine. I said as much in last post, and nearly said it in my first. Just, as I'm sure you would, make sure it's suitably sleeved so it can be obviously identified at both ends by yourself and any future authority or whoever takes on the property after you...
Quote:Have spent the morning searching through various forums on this subject, it's alarming to read so many cavalier responses to questions on electrical safety.
I will try and find the IEE link to that PME article and post it, as I am sure many of us have outside sheds/ workshops etc that have or thinking of having electricity supply feeds.
Yes, I've probably spent more than a couple of hours on this as well. Of all the topics that come up, this is one of the more complicated ones, and it's good to discuss it.
All the best,
Mark