Hello Mark, the reason for gravity flow in solid fuel/wood fired boilers is for safety reasons, there must be nothing in the primary HW flow system than in any remotely possible way can impede the thermal flow and thus circulation of the hot back down to cool flow.
If for instance there was installed a solenoid operated Y valve and it jammed open in the CH position and the CH pump had stopped working ie: prolonged power failure (bad scenario) then that would mean that the primary HW flow would cease to flow, the water temp. in the boiler would quickly rise until it turned to steam, the laws of thermo dynamics take over and bang, possible shrapnell through any soft objects in the way, they have been know to blow the back wall of the fireplace reccess right out.
With gas or oil fired once the supply is shut off this will not happen, these types of boilers have a permanent temp. sensor possibly capillary that shut the fuel supply and/or burner off instantly, the same as the "fire" valve in an oil feed supply line between the oil tank and the boiler.
With solid fuel/ wood you cannot shut the heat off instantly, there might be systems now that do, I don't know, but personaly i would only have a full gravity primary flow system as it is pretty much tried and tested.
PS I am not a plumber, any propposed diy heating then need to satisfy regs/safety yourselves.
Lawrence.
If for instance there was installed a solenoid operated Y valve and it jammed open in the CH position and the CH pump had stopped working ie: prolonged power failure (bad scenario) then that would mean that the primary HW flow would cease to flow, the water temp. in the boiler would quickly rise until it turned to steam, the laws of thermo dynamics take over and bang, possible shrapnell through any soft objects in the way, they have been know to blow the back wall of the fireplace reccess right out.
With gas or oil fired once the supply is shut off this will not happen, these types of boilers have a permanent temp. sensor possibly capillary that shut the fuel supply and/or burner off instantly, the same as the "fire" valve in an oil feed supply line between the oil tank and the boiler.
With solid fuel/ wood you cannot shut the heat off instantly, there might be systems now that do, I don't know, but personaly i would only have a full gravity primary flow system as it is pretty much tried and tested.
PS I am not a plumber, any propposed diy heating then need to satisfy regs/safety yourselves.
Lawrence.