OK this is for any electroplumbers out there, I designed and fitted the central heating system in the house we now live in, it's wood powered.
The boiler in the woodstove is a cross flow ie: two diagonal outlets (flow and return) for the primary water heating (28mm) gravity flow to and from the HW tank (Indirectly heated ie: coil inside)
The other two diagonal outlets feed (flow and return) 8 radiators via CH pump.
I designed the system so that the radiators only come on when the HW tank has reached a mean temp of 60 degrees C, the CH pump then kicks in ie: priority hotwater.
I have a minimum temperature thermostat fitted to the CH return pipe within 6" of the boiler, it is set so that the CH pump switches off if the water temp in the stove boiler drops below a certain low level, this is to help reduce the possibility of condensation on the fire box side of the boiler if the wood contains any significant moisture.
There is a high set temp. thermostat within 6" of the boiler on the HW gravity flow pipe, this is set to about 85-90 degrees C so that if the gravity flow has not got the HW tank to its mean 60 degrees then the CH pump will kick in before the boiler starts gassing or boiling the resulting CH flow will then reduce the water temp in the boiler to a lower level ie: dump the excsesive heat.
The system is fitted with the correct size expansion pipes etc and a permenant heatsink radiator in parrallel with the HW flow and return to/from the HW tank.
The problem is the last mentioned set high temp thermostat, it is a standard bi metal Honeywell job which is retained on the pipe by its own built in springs.
The problem being that if the fire is started from cold with dry wood then the HW flow pipe beween the boiler and the HW tank can attain a high temperature very quickly, the pipe can get to almost boiling before full gravity circulation takes place, this is partly my design problem as we are limited to how high the HW tank can be physically located above the boiler and there is nothing I can do about that.
So as I was saying the flow pipe can attain near boiling temp before full gravity flow takes place, if this temp is attained quickly then the water in the boiler will start to "gass" and almost boil before the high limit temp stat kicks in, this is due to the relatively slow thermal conduction through the stats interface with the HW flow pipe and then up on through the stat to the bi metal strip.
If the fire is built up slowly from scratch then this rapid heating of the HW flow pipe is not a problem.
So in all this I need a quicker reacting (temp. transfer wise) stat that is not going to cost a dissproportionate amount of money.
Any one got any ideas?
The stat has only got to switch the current flowing through the CH pump, the pump is a standard Grundfos CH pump set to low flow (position 1) and passes less than an amp as far as I am aware.
Lawrence.
The boiler in the woodstove is a cross flow ie: two diagonal outlets (flow and return) for the primary water heating (28mm) gravity flow to and from the HW tank (Indirectly heated ie: coil inside)
The other two diagonal outlets feed (flow and return) 8 radiators via CH pump.
I designed the system so that the radiators only come on when the HW tank has reached a mean temp of 60 degrees C, the CH pump then kicks in ie: priority hotwater.
I have a minimum temperature thermostat fitted to the CH return pipe within 6" of the boiler, it is set so that the CH pump switches off if the water temp in the stove boiler drops below a certain low level, this is to help reduce the possibility of condensation on the fire box side of the boiler if the wood contains any significant moisture.
There is a high set temp. thermostat within 6" of the boiler on the HW gravity flow pipe, this is set to about 85-90 degrees C so that if the gravity flow has not got the HW tank to its mean 60 degrees then the CH pump will kick in before the boiler starts gassing or boiling the resulting CH flow will then reduce the water temp in the boiler to a lower level ie: dump the excsesive heat.
The system is fitted with the correct size expansion pipes etc and a permenant heatsink radiator in parrallel with the HW flow and return to/from the HW tank.
The problem is the last mentioned set high temp thermostat, it is a standard bi metal Honeywell job which is retained on the pipe by its own built in springs.
The problem being that if the fire is started from cold with dry wood then the HW flow pipe beween the boiler and the HW tank can attain a high temperature very quickly, the pipe can get to almost boiling before full gravity circulation takes place, this is partly my design problem as we are limited to how high the HW tank can be physically located above the boiler and there is nothing I can do about that.
So as I was saying the flow pipe can attain near boiling temp before full gravity flow takes place, if this temp is attained quickly then the water in the boiler will start to "gass" and almost boil before the high limit temp stat kicks in, this is due to the relatively slow thermal conduction through the stats interface with the HW flow pipe and then up on through the stat to the bi metal strip.
If the fire is built up slowly from scratch then this rapid heating of the HW flow pipe is not a problem.
So in all this I need a quicker reacting (temp. transfer wise) stat that is not going to cost a dissproportionate amount of money.
Any one got any ideas?
The stat has only got to switch the current flowing through the CH pump, the pump is a standard Grundfos CH pump set to low flow (position 1) and passes less than an amp as far as I am aware.
Lawrence.