(12-11-2013, 01:42 PM)pwdrive Wrote: Refugees suggestion sounds the cheapest, either that or a helipot for a more broad control over the min to max speed as has been previously suggested.
Its not only not the cheapest (it has an extra resistor) - its not the way the unit is intended to be used - the VFD drive has a bunch of parameters set via the control panel that set things like the output voltage and frequency range it generates - messing with the input voltage range is most certainly not the way to resolve this - the issue is that the VFD drive needs to be set up for the motor and application its intended for - this is done via the control panel and parameter settings as laid out in the manual, which, incidentally, is not at all bad - the English is good and its pretty concise,
This is a decent, PID-controlled, VFD - a semi-professional bit of kit designed for a very wide range of loads, hence it needs configuring/commissioning prior to use.
As we are using voltage control, A1 is not used if PD070 = "0" (the default) and external control is enabled by setting PD02 = "1" (*not* the factory default).
If PD02 is not = "1" I'm not sure why V1 is having any effect at all...
Manual attached (library at http://www.etech.net.au/Huanyang/)
sıʌǝɹq ɐʇıʌ `ɐƃuol sɹɐ
ʞɔıu
ʞɔıu


That was tongue-in-cheek - its just that that is simply not the way to fix this issue - its a hack, and a bad one at that.