I have several 12V halogen spots in my workshop. They were originally supplied from a horrible radiating switch-mode supply. I replaced that with a nice clean toroidal 300W transformer so that I could once again use my AM radios.
Unfortunately, the inrush current on switching on the lights would then often cause the RCD to trip, depending, I guess, on the direction of the core's residual magnetisation after it was last switched off. The solution was to fit a suitably rated NTC thermistor in series with the transformer mains primary to limit the inrush current.
Martin
Unfortunately, the inrush current on switching on the lights would then often cause the RCD to trip, depending, I guess, on the direction of the core's residual magnetisation after it was last switched off. The solution was to fit a suitably rated NTC thermistor in series with the transformer mains primary to limit the inrush current.