15-09-2015, 04:11 PM
(This post was last modified: 15-09-2015, 04:24 PM by SurreyNick.)
Mod Edit: When testing a mains transformer, especially an unknown one, great care is required. Although not stated in the opening post, Nick tested this transformer using a low voltage (10V), and scaled up the measured voltages accordingly. This is an excellent approach, and one which should be considered if you need to do a similar thing. If in any doubt about how to safely test a transformer, or indeed have any safety-related concerns about topic, please ask for help - that's what the forum is here for 
I am confused. (It doesn't take much it seems!)
I have been given this salvaged transformer (see pics) and I want to label up the various windings and tap voltages. The difficulty I have is that I have no idea which winding was what, nor what the values of the various taps should have been and my naff DMM is giving me some rather odd values. I have attached a PDF with the various readings (ohms and volts) that I have obtained.
As you can see from the two pictures the transformer has four tag strips and there are five windings.
Tag strip A with its two tags I have named winding 1 and I have assumed this is the primary winding.
Tag strip B has one winding with five tags. I have named this winding 2. I get 240v across the first and last tag, which suggests a 1:1 ratio with the primary. The other values are shown in the attached PDF.
Tag strip C is two windings, one with three tags (winding 3) and one with two tags (winding 4). With winding 3 I get 1248v across the first and last tag with 624v between the centre tap and each end tag. This seems absurdly high. I get 10v between the two tags of winding 4.
Tag strip D is one winding with three tags. I have named this winding 5. It has continuity but I get zero volts. When I got the transformer the centre tap of this winding was strapped to the centre tap of winding 3 and when strapped I get continuity across the two windings but still no voltage! The ohms reading is very small and I'm wondering if this is a low voltage filament or rectifier winding and my naff DMM, which won't zero on AC Volts just can't get a low enough reading.
I guess my questions are:
1. Have I assumed correctly that winding one is the primary?
2. Do the readings seem reasonable - even the 1248v reading?
The benefit of your knowledge and experience would be most helpful.
Thanks
Nick
Philips Power Transformer schematic.pdf (Size: 223.7 KB / Downloads: 47)
I am confused. (It doesn't take much it seems!)
I have been given this salvaged transformer (see pics) and I want to label up the various windings and tap voltages. The difficulty I have is that I have no idea which winding was what, nor what the values of the various taps should have been and my naff DMM is giving me some rather odd values. I have attached a PDF with the various readings (ohms and volts) that I have obtained.
As you can see from the two pictures the transformer has four tag strips and there are five windings.
Tag strip A with its two tags I have named winding 1 and I have assumed this is the primary winding.
Tag strip B has one winding with five tags. I have named this winding 2. I get 240v across the first and last tag, which suggests a 1:1 ratio with the primary. The other values are shown in the attached PDF.
Tag strip C is two windings, one with three tags (winding 3) and one with two tags (winding 4). With winding 3 I get 1248v across the first and last tag with 624v between the centre tap and each end tag. This seems absurdly high. I get 10v between the two tags of winding 4.
Tag strip D is one winding with three tags. I have named this winding 5. It has continuity but I get zero volts. When I got the transformer the centre tap of this winding was strapped to the centre tap of winding 3 and when strapped I get continuity across the two windings but still no voltage! The ohms reading is very small and I'm wondering if this is a low voltage filament or rectifier winding and my naff DMM, which won't zero on AC Volts just can't get a low enough reading.
I guess my questions are:
1. Have I assumed correctly that winding one is the primary?
2. Do the readings seem reasonable - even the 1248v reading?
The benefit of your knowledge and experience would be most helpful.
Thanks
Nick
Philips Power Transformer schematic.pdf (Size: 223.7 KB / Downloads: 47)