15-02-2021, 08:33 AM
A friend phoned me the other day saying their dishwasher was dead and could I help. I was a bit reluctant but asked the relevant questions and got them to take a shot of the connections when it was pulled out. The flex went via a "tape bomb" to a flex outlet plate. it had its own MCB in the consumer unit. I got them to check that all was secure inside the tape bomb.
While it's not a true domestic emergency I decided on balance that I could go and have a look. Especially as the presence of a tape bomb sugegsted there might be a genuine hazard. I had to repeat measurements several times to convince myself about what I'd found. Both live and neutral were open circuit between the CU and the outlet. Earth was OK but that could have been a fortuitous path. The presumed cable route was over the ceiling and down so my though was that the upstairs neighbour had done something silly unde their floorboards. This was denied. If it had been just one core then I might have believed mice though 2.5mm T+E would be pretty tough for them. Neither the RCD nor MCB (16A) had tripped.
I am truly puzzled byt this one. I wonder if I will ever find the true cause of the fault.
I did resolve the tape bomb. They'd had a new (to them) dishwasher installed. The installer should have fitted a socket instead of the flex outlet plate but wired the new machine into the flex outlet. Subsequently the machine had been taken away for repair. The repairer had obviously just cut the flex and used a tape bomb to rejoin it.
The immediate fix was putting a plug on the flex and using an extension to connect it to another socket. I also disconencted the circuit at the CU. The long term fix will be a new socket on the kitchen ring whose cables pass close by and are readily accessible. The kitchen ring doesn't have any other heavy loads so it will be fine.
While it's not a true domestic emergency I decided on balance that I could go and have a look. Especially as the presence of a tape bomb sugegsted there might be a genuine hazard. I had to repeat measurements several times to convince myself about what I'd found. Both live and neutral were open circuit between the CU and the outlet. Earth was OK but that could have been a fortuitous path. The presumed cable route was over the ceiling and down so my though was that the upstairs neighbour had done something silly unde their floorboards. This was denied. If it had been just one core then I might have believed mice though 2.5mm T+E would be pretty tough for them. Neither the RCD nor MCB (16A) had tripped.
I am truly puzzled byt this one. I wonder if I will ever find the true cause of the fault.
I did resolve the tape bomb. They'd had a new (to them) dishwasher installed. The installer should have fitted a socket instead of the flex outlet plate but wired the new machine into the flex outlet. Subsequently the machine had been taken away for repair. The repairer had obviously just cut the flex and used a tape bomb to rejoin it.
The immediate fix was putting a plug on the flex and using an extension to connect it to another socket. I also disconencted the circuit at the CU. The long term fix will be a new socket on the kitchen ring whose cables pass close by and are readily accessible. The kitchen ring doesn't have any other heavy loads so it will be fine.